Combustion Air Switch Failed to Close

Postby freddy6282 » Thu Nov 04, 2010 3:43 pm

I have a furnace model DGAT056BDF that worked fine last winter but when i tried to turn it on for the first time this year, it wouldn't start and showed 3 flashing lights for the error code, which on my furnace reads "Combustion air switch failed to close" I couldn't hear the pressure switch clicking or sealing off when it was on, yet was getting voltage to the terminals, so i tried replacing the pressure switch with no success. What parts should i be looking at, or what else could be causing the error code to come up? Any help would be greatly appreciated!

Thank You!
Freddy
freddy6282
 
Posts: 3
Joined: Thu Nov 04, 2010 3:33 pm

Re: Combustion Air Switch Failed to Close

Postby Robert » Fri Nov 05, 2010 10:51 pm

Blockage or leak in combustion air pipe, combustion motor or wheel faulty-dirty, tubes to pressure kinked, loose or clogged.

IF all ok, 24vac to one of the two wires at switch and a new switch installed, time to call an hvac tech.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
User avatar
Robert
Moderator
 
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Re: Combustion Air Switch Failed to Close

Postby freddy6282 » Sat Nov 06, 2010 3:44 am

Thanks I'll check to make sure the motor and wheel aren't dirty, tubes look to be fine. Appreciate the help!
freddy6282
 
Posts: 3
Joined: Thu Nov 04, 2010 3:33 pm

Re: Combustion Air Switch Failed to Close

Postby freddy6282 » Sat Nov 06, 2010 12:38 pm

For anyone else who might be having the same problem as I had...It was indeed the fan on the combustion blower, it was seized up and needed to be cleaned and lubricated.
freddy6282
 
Posts: 3
Joined: Thu Nov 04, 2010 3:33 pm

Re: Combustion Air Switch Failed to Close

Postby Robert » Sun Nov 07, 2010 1:13 am

Hi,

You're very welcome, happy to help. Glad it is taken care of.


Thanks,
Robert