I have the subject furnace and recently replaced the pressure switch. Now when I turn on the furnace it will cycle 3 times and shut down. The control module light now flashes 4 times. Do know what the problem may be now?
Thanks
Nordyne Model# M1MB 070A BW
The board in your furnace is a 903429. Below are the codes for that board:
Red light:
Steady on - OK
Rapid Flash - False flame or internal control fault.
1 Flash - Limit switch open.
2 Flash - Pressure switch open w/ inducer on.
3 Flash - Pressure switch closed w/ inducer off.
4 Flash - Lockout due to failed ignition.
5 Flash - Reversed polarity.
Yellow Light:
Steady On - Good flame signal.
Blinking - Weak flame signal.
Steady Off - No flame signal.
Red light:
Steady on - OK
Rapid Flash - False flame or internal control fault.
1 Flash - Limit switch open.
2 Flash - Pressure switch open w/ inducer on.
3 Flash - Pressure switch closed w/ inducer off.
4 Flash - Lockout due to failed ignition.
5 Flash - Reversed polarity.
Yellow Light:
Steady On - Good flame signal.
Blinking - Weak flame signal.
Steady Off - No flame signal.
You can't fail if you don't try!
Hi,
3 most common are the Hot Surface Ignitor, Remote Flame Sensor or the Gas Valve.
I believe your furnace HSI is also the flame sensor, would have to look to be sure .
Thanks,
Robert
3 most common are the Hot Surface Ignitor, Remote Flame Sensor or the Gas Valve.
I believe your furnace HSI is also the flame sensor, would have to look to be sure .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Please start a new thread and then delete this post. We keep threads to original poster for ease of following.
Thanks,
Robert
Please start a new thread and then delete this post. We keep threads to original poster for ease of following.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne model m1mb 070a bw power issue
by Combustibleink » Mon Nov 16, 2020 10:21 am » in Nordyne Service & Repair - 0 Replies
- 95081 Views
-
Last post by Combustibleink
Mon Nov 16, 2020 10:21 am
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 38101 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 97387 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Evcon Heat Pump - Air Conditioner Model No. BRHS036B Making HUM Before Starting
by Dave_L » Tue Aug 29, 2023 1:26 am » in Coleman Service & Repair - 0 Replies
- 100042 Views
-
Last post by Dave_L
Tue Aug 29, 2023 1:26 am
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 24692 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-