I have a Nordyne M1MD 070A BW. When I started it up this winter
everything seems to work fine, I have induction, ignition, flame, blower but the air temp coming out of the registers is only 78 degrees. The filter is clean, the flame looks O.K., and the gas pressure has been checked and is O.K. Everything is the same as last year except that I am not getting the heat out of the unit. This is driving me nuts. Any ideas what to check or what it could be.
Runs Fine No Heat
Hi,
Check the main burner orifice for clogs (spider/web). If it is ok, make sure there is not damage to duct allowing loos of heat or infiltration of cool air.
Thanks,
Robert
Check the main burner orifice for clogs (spider/web). If it is ok, make sure there is not damage to duct allowing loos of heat or infiltration of cool air.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I pulled the main burner assembly to clean the orifice. When I removed the orifice and looked down the spud I saw a what looks like a clear plastic membrane with a hole in the middle of it. I could not find this on the parts list for the furnace or the service manual. I did not remove it but was wondering if this is suppose to be there and if so what is the name of it? Also what temperature air should be coming out of the registers when this furnace is running right?
It was inside where ? Look on data sticker for Temp Rise and measure that to see if temp is correct at registers.
Thanks,
Robert
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 22638 Views
-
Last post by nestsman
Sat Aug 19, 2017 1:47 pm
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 52036 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Acceptable HEAT RISE number for this 20-yr. old furnace.
by justplumducky » Tue Aug 29, 2017 5:33 pm » in Nordyne Service & Repair - 0 Replies
- 41895 Views
-
Last post by justplumducky
Tue Aug 29, 2017 5:33 pm
-
-
- 0 Replies
- 40160 Views
-
Last post by David DeBord
Sun Oct 22, 2017 7:13 am
-
-
A/C and heat comes from the ceiling vents. Are the existing floor vents necessary?
by NanaMary » Tue Nov 21, 2017 12:35 pm » in All Other HVAC Questions - 2 Replies
- 52860 Views
-
Last post by NanaMary
Fri Nov 24, 2017 11:14 am
-