I have a e2eb-012ha with 4 speed blower fan. When the furnace makes a call for heat the t-stat clicks, fan kicks on, but delivery is room temperature or cooler. Fan kicks on and off as would be expected if temperature is adjusted above an below the current temperature. I.e. kicks off if set for 70 and t-stat shows room at 75, kicks on if set for 80 and room at 75.
Looked inside the heating core and the coils do not seem to be heating. Sequencer appears to be good.
Any other possibilities beside elements going out that the coils would not be heating?
Thanks
Transformer, and limit switches appear to be good as well when tested with meter.
Nordyne e2eb-012ha no heat
Hi,
What do you mean by "sequencer appears to be good" ? When you looked at the elements, are you sure that NONE of them are energized ?
Did you test all the elements at the front plates to see if any were getting power ?
It would be rare for them ALL to fail at same time. So, need to be sure that there isn't at least one working.
Thanks,
Robert
What do you mean by "sequencer appears to be good" ? When you looked at the elements, are you sure that NONE of them are energized ?
Did you test all the elements at the front plates to see if any were getting power ?
It would be rare for them ALL to fail at same time. So, need to be sure that there isn't at least one working.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
I put a meter to sequencer, limit switch, breakers, blower relay, transformer, and both element coils and the Ohm meter checked them as fine. I have a tech coming out today to look at it.
Thank you for your help.
Thank you for your help.
Hi,
You're very welcome, happy to help. Would need to know what is and is not receiving voltage.
Take care and best wishes,
Robert
You're very welcome, happy to help. Would need to know what is and is not receiving voltage.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 23416 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 41656 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 62385 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
- 0 Replies
- 22404 Views
-
Last post by nestsman
Sat Aug 19, 2017 1:47 pm
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 51049 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-