Thermal Zone (Nordyne) not starting

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
Skunkbear
Posts: 1
Joined: Fri Jan 16, 2009 5:44 pm
Location: Michigan

Furnace Model GU060m12A-S will work at times but not at others. History - Furnace stopped a couple of days ago, I was getting an error of 3 red flashes which means "pressure switch closed with inductor on". If I remove the down draft vent this goes away but the furnace will stil not work all the time. This afternoon I replace the hot surface ignitor (because I broke the other one) and it ran for about 4 cycles now the furnace goes until the ignitor glows I can hear the gas flow thru the valve (honeywell) but no ignition.
Any ideas?
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Start at beginning and deal with the pressure switch problem.

Could be a bad pressure switch, clogged or damaged vent air pipe, bad inducer motor, clogged, kinked, loose or damaged pressure tubes.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?