I have a single package unit outside, when the temps are down, I used to be able to manually turn on the "emergency heat" , now when i do it it starts to blow colder air than before.
In normal mode, it seems to be running fine......what gives?
also, is the light for emergency heat supposed to come on when you increase the thermostat for more heat? It does not now, & never has!
To end this question, I had to have a tech come out & replace some duct work & he cleaned the coils inside with water....washed them out.....any of these problems could have arose since he came or does it sound like it has had problems all along.....with how things are wired/working?
Thanks
Tim
Intertherm....problems
There are several things that happen when you switch to emergency heat. First your compressor and outdoor fan(not your indoor blower) should shut off and stay off the entire time you have it in the emergency heat mode. Second your heat strips and indoor blower should cycle together when ever your t-stat calls for heat unless you have your fan switch on the t-stat in the "on" position instead of auto. If you have cold air when you are in the Em.HT mode your problem could be with the heat strips, contactor or seqencer, your t-stat and any wiring connecting any of these devices. As for the Em-Ht light some t-stat require an additional wire to illuminate the bulb and that wire may not be there or improper wiring of the t-stat may have occurred. There are so many t-stats you can use it's hard to tell without the wiring diagram for your particular stat.
Hi Tim,
Cleaning the A-Coil inside with use of water is fine, but can ruin contactors, sequencers and heat strips if not real careful.
I'm suspecting that it shuts down compressor and condenser fan and you get the blower, but no heat strips, thus reason for colder air due to now having no heat input.
Thanks,
Robert
Cleaning the A-Coil inside with use of water is fine, but can ruin contactors, sequencers and heat strips if not real careful.
I'm suspecting that it shuts down compressor and condenser fan and you get the blower, but no heat strips, thus reason for colder air due to now having no heat input.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 0 Replies
- 43961 Views
-
Last post by chrismc_us
Mon Dec 23, 2019 9:00 am
-
-
2-combo single pole lightswitch problems
by hstassen » Mon Jan 06, 2020 9:41 pm » in Mobile Home Repair - 2 Replies
- 12818 Views
-
Last post by Greg
Tue Jan 07, 2020 6:12 pm
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 51976 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 71273 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 112112 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-