Nordyne furnace keeps running
I have a Nordyne M1Mb 056A BW and just recently replaced the thermostat, but when I did the furnace stays on after the click when it reaches temp. I reinstalled the old one, and it does the same thing. It comes on fine, then lights, then blows, when temp. is reached, it clicks at thermostat, then blows for minutes longer, then will shut off sometimes, or sometimes will just relight and come back on. Please help..thanx..
Hi,
You don't have a sequencer. Could be faulty ignition module or control board.
Would need to be able to test voltage to find problem or call an hvac tech to diagnose.
Start at gas valve and test for 24vac and work backwards following wiring diagram to locate where low voltage is remaining energized.
Thanks,
Robert
You don't have a sequencer. Could be faulty ignition module or control board.
Would need to be able to test voltage to find problem or call an hvac tech to diagnose.
Start at gas valve and test for 24vac and work backwards following wiring diagram to locate where low voltage is remaining energized.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Test to locate which limit is open. Then determine if furnace is overheating/HOT.
If so, call an hvac tech. If not (furnace has been on in long while for instance), replace limit.
Can give ordering info this evening if needed.
Thanks,
Robert
If so, call an hvac tech. If not (furnace has been on in long while for instance), replace limit.
Can give ordering info this evening if needed.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 36153 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
-
Heat strip on while AC is running HELP Please!
by HelpNeeded » Wed Sep 19, 2018 6:47 pm » in Coleman Service & Repair - 0 Replies
- 30903 Views
-
Last post by HelpNeeded
Wed Sep 19, 2018 6:47 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 152258 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 42235 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 28210 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-