Nordyne E2EB-015HA blower needs replacing
I currently have a Nordyne furnace model E2EB-015HA with a blower assembly marked as 902993 . I was wondering if I should/could replace it with the 902985 blower assembly. Would this be compatible and provide better air flow thru the house? The blower assembly needs to be replaced and not sure which would be best.
Hi,
902993 is for 2 to 4 tons of cooling.
902985 is for 5 tons of cooling.
What tonnage is your a/c ?
Thanks,
Robert
902993 is for 2 to 4 tons of cooling.
902985 is for 5 tons of cooling.
What tonnage is your a/c ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
The outside unit is Nordyne js3ba 048ka. I'm embarassed to say that it is plainly marked 4 ton right in plain sight. so if it calls for a 902993 would the 902985 not cool properly on a 4 ton unit? My home has 13 vents and was just wondering if the 5 ton unit would provide better air flow?
Hi,
The 902985 is a 5 ton blower and provides 5 tons of airflow. It would require 5 tons of cooling capacity.
The 902993 is what your a/c is designed for.
IF the airflow or cooling is not adequate, have an hvac tech to run some tests to see what the problem is.
Could be low charge, dirty coil, filter or blower wheel, motor going bad, duct problems, wrong size a/c unit, etc... .
Thanks,
Robert
The 902985 is a 5 ton blower and provides 5 tons of airflow. It would require 5 tons of cooling capacity.
The 902993 is what your a/c is designed for.
IF the airflow or cooling is not adequate, have an hvac tech to run some tests to see what the problem is.
Could be low charge, dirty coil, filter or blower wheel, motor going bad, duct problems, wrong size a/c unit, etc... .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 161351 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 63191 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
- 1 Replies
- 3516 Views
-
Last post by Norm Frechette
Mon Sep 04, 2017 5:49 am
-
- 0 Replies
- 25811 Views
-
Last post by MobileMatt
Mon Jan 07, 2019 9:03 pm
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 37645 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-