Hello,
I have a Nordyne C1QA-030U-B, a furnace with a/c. Nothing is working. No heat, no a/c, and the fan will not come on when switched from "auto" to on.
I have replaced the thermostat, and checked to make sure the breakers inside the house are in the "on" position. Still nothing.
Please help, it is getting hotter outside.
Thanks,
Ric
Nordyne won't turn on
Hi Ric,
Test primary-line side of transformer for 120vac or 240vac.
If there, test secondary-load side for 24-28vac.
Either transformer has blown, a fuse has blown or a loose wire on power or neutral side of 24vac low voltage circuit.
Thanks,
Robert
Test primary-line side of transformer for 120vac or 240vac.
If there, test secondary-load side for 24-28vac.
Either transformer has blown, a fuse has blown or a loose wire on power or neutral side of 24vac low voltage circuit.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 152294 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
In too deep to turn back now... now what?
by Do it herselfer » Thu Nov 02, 2017 11:28 pm » in Mobile Home Repair - 2 Replies
- 24464 Views
-
Last post by yakima4$
Tue Dec 05, 2017 8:29 pm
-
-
- 2 Replies
- 16974 Views
-
Last post by TorstenW
Tue Mar 06, 2018 1:04 am
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 158433 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 42244 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-