I have a Nordyne MGHA-070ABFC-05 (serial: MGH9510-04280) which is a split unit (AC and heat in one unit). We installed a new t-stat (Honeywell programmable) thinking that was the issue but am still having the same issue. The old t-stat was a mercury style w/a heat/off/cool selection.
Issue is when we set the t-stat to a certain temp, the AC continues to run even after it reaches the designated temp. I found that I have to manually operate the t-stat in order to turn on/off the AC. I found the only way to turn off the AC is to turn the t-stat to 'heat', or to switch off the breaker power supply to the unit. (Even when I switch the t-stat to 'off', it still continues to run. The AC continuously runs cold air even after it reaches the temp selected.
Any ideas what could be causing this?
Oh, there are only 2 wires that run to the t-stat (white and red). We tried hooking them up different ways on the t-stat but we either run into the same issue where you have to switch it to heat to turn off, or it continues to run until we flip the breaker.
The furnace runs fine!
AC not shutting off
Hi,
You have a 2 wire set up. Wall t-stat should remain in HEAT selection year round.
Then, the two switches at furnace should be set to the season, HEAT for winter and COOL for summer and fan switch to AUTO always.
Otherwise, you will need to replace 2 wire control box with a 5 wire box and run 5 wire t-stat wire to t-stat which will need to be a 5 wire t-stat for your furnace and a/c system.
During summer, a t-stat reversing relay in the a/c control box controls the a/c system.
With switches set as stated, set temp where it is wanted and system should turn itself off and on as desired.
Thanks,
Robert
You have a 2 wire set up. Wall t-stat should remain in HEAT selection year round.
Then, the two switches at furnace should be set to the season, HEAT for winter and COOL for summer and fan switch to AUTO always.
Otherwise, you will need to replace 2 wire control box with a 5 wire box and run 5 wire t-stat wire to t-stat which will need to be a 5 wire t-stat for your furnace and a/c system.
During summer, a t-stat reversing relay in the a/c control box controls the a/c system.
With switches set as stated, set temp where it is wanted and system should turn itself off and on as desired.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 105311 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 150790 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 35388 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
- 1 Replies
- 36753 Views
-
Last post by Greg
Sat Jan 06, 2018 9:11 am
-
-
Intertherm FEH-017HAC won't shut off
by Jetherid » Mon Dec 07, 2020 6:22 pm » in Nordyne Service & Repair - 0 Replies
- 156901 Views
-
Last post by Jetherid
Mon Dec 07, 2020 6:22 pm
-