Nordyne mod. # MT30C-042K condensing unit control board

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
jescoman
Posts: 2
Joined: Wed Aug 18, 2010 10:36 pm

Checked unit and found 24 volts to board, but not running, nor contactor pulled in. Removed and re-installed ODT and unit came on. Worked OK till customer had power outage, when power returned, condensing unit failed to come on. Removed ODT and bypassed, came on fine until a another utility related power failure again. Again found condensing unit off. Removed and replaced jumper and unit runs. Do I have board issues and if so is that board model # 917178A?
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

IF you have low voltage to board, BUT not out of board to contactor, then unless there is a timer on board delaying it, it is bad.

With it only happening with a power outage, sounds more like a delayed timer issue.



Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
jescoman
Posts: 2
Joined: Wed Aug 18, 2010 10:36 pm

Is the board part # for this unit in fact 917178A? Thanks for your help. Unit model # is actually MT3QC-042K. Thanks!
Scott J.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

Yes, 917178A is correct defrost control board number.



Thanks,
Robert