Blower continues to run in low speed when air is off

Posted: Tue Aug 21, 2007 8:55 am
by felise
Hello,
I'm having some issues with the blower on my AC. I can't find the model # but it reads Intertherm on the front cover and the blower and coil read Nordyne on them. It's in a mid 90's Palm Harbor manufactured home. It's a total electric split system.

The blower runs all of the time except that when I turn the air off at the thermostat, the blower speed slows down to about half speed. The only way that I can shut off the blower is to shut off the breaker. It just started doing this yesterday.


Any ideas what I should check first?

Thanks!

EDIT: I found the model # E1EB-015HA

RE: Blower continues to run in low speed when air is off

Posted: Tue Aug 21, 2007 12:41 pm
by Robert
Hi,

Most likely a stuck contact on your Blower Relay.

To test, locate relay and test across terminals 1 and 3 for 24vac.

You should read 0vac .

Then test across 2 and 4 for 240vac .

You should read 240vac.


It can be seen and ordered from this page:

http://www.mobilehomerepair.com/NordyneElec.html


Blower Relay # 621867 @ $13.53 + $6.75 shipping


Scroll down left side to locate, click on pic for enlarged view.


If interested, please add item to cart and order through PayPal or call toll free to 1-877-263-7860 and charge to Visa or Mastercard.


Thanks for inquiring and allowing us to assist you.


Take care and best wishes,
Robert

Posted: Wed Aug 22, 2007 9:29 am
by felise
Thanks Robert. I found one of your old post about testing the relay which I did and sure enough, it's bad.

Thanks again for the help!

RE: Blower continues to run in low speed when air is off

Posted: Wed Aug 22, 2007 9:17 pm
by Robert
Hi,

You're very welcome, glad you found the problem.

Take care and best wishes,
Robert