Hello,
I'm having some issues with the blower on my AC. I can't find the model # but it reads Intertherm on the front cover and the blower and coil read Nordyne on them. It's in a mid 90's Palm Harbor manufactured home. It's a total electric split system.
The blower runs all of the time except that when I turn the air off at the thermostat, the blower speed slows down to about half speed. The only way that I can shut off the blower is to shut off the breaker. It just started doing this yesterday.
Any ideas what I should check first?
Thanks!
EDIT: I found the model # E1EB-015HA
Blower continues to run in low speed when air is off
Hi,
Most likely a stuck contact on your Blower Relay.
To test, locate relay and test across terminals 1 and 3 for 24vac.
You should read 0vac .
Then test across 2 and 4 for 240vac .
You should read 240vac.
It can be seen and ordered from this page:
http://www.mobilehomerepair.com/NordyneElec.html
Blower Relay # 621867 @ $13.53 + $6.75 shipping
Scroll down left side to locate, click on pic for enlarged view.
If interested, please add item to cart and order through PayPal or call toll free to 1-877-263-7860 and charge to Visa or Mastercard.
Thanks for inquiring and allowing us to assist you.
Take care and best wishes,
Robert
Most likely a stuck contact on your Blower Relay.
To test, locate relay and test across terminals 1 and 3 for 24vac.
You should read 0vac .
Then test across 2 and 4 for 240vac .
You should read 240vac.
It can be seen and ordered from this page:
http://www.mobilehomerepair.com/NordyneElec.html
Blower Relay # 621867 @ $13.53 + $6.75 shipping
Scroll down left side to locate, click on pic for enlarged view.
If interested, please add item to cart and order through PayPal or call toll free to 1-877-263-7860 and charge to Visa or Mastercard.
Thanks for inquiring and allowing us to assist you.
Take care and best wishes,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks Robert. I found one of your old post about testing the relay which I did and sure enough, it's bad.
Thanks again for the help!
Thanks again for the help!
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Furnance continues to click, Fan always on
by rcrown1872 » Tue Oct 01, 2019 11:55 am » in Nordyne Service & Repair - 0 Replies
- 22007 Views
-
Last post by rcrown1872
Tue Oct 01, 2019 11:55 am
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 20579 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-
-
-
Can't read MFD size on rusted dual run cap.
by justplumducky » Sat Jul 01, 2017 6:31 pm » in Nordyne Service & Repair - 0 Replies
- 41008 Views
-
Last post by justplumducky
Sat Jul 01, 2017 6:31 pm
-
-
-
Ideas for A Low Bugdet Furnace
by lpaigeg268 » Mon Apr 02, 2018 10:36 pm » in Service & Repair of Other Brands - 2 Replies
- 19867 Views
-
Last post by lpaigeg268
Sun Jul 07, 2019 10:13 pm
-
-
-
Are low taxes worth investing into a old mobile home to make it more energy efficient?
by spazatac » Sun Jun 30, 2019 11:30 am » in Off Topic Discussions - 2 Replies
- 26142 Views
-
Last post by spazatac
Sat Jul 06, 2019 6:47 pm
-