Posted: Tue Feb 27, 2007 11:20 pm
by rogerman123
I have a nordyne E2EB-015HR I WAS TOLD IT NEEDS SEQUENCERS AND A FAN RELAY....IT WILL COST $1100.00...CAN YOU HELP ME GET THE PARTS?

Posted: Wed Feb 28, 2007 1:34 am
by Robert
Hi,

We have the parts. The Sequencer and Relay plus shipping totals $60.

If you are slightly handy with tools/repairs, this is a definate DIY task.

$1,100 is a rip and absurd.

What is the furnace doing in case it was misdiagnosed ?


Take care and best wishes,
Robert

Posted: Wed Feb 28, 2007 6:05 pm
by rogerman123
the furnace will come on when you set the thermostat.....it stays on for about 5 min. then it shuts off for about 2 min. until it reaches the temp you set on the thermostat.

Posted: Wed Feb 28, 2007 6:07 pm
by rogerman123
it does that continually untill it reaches temp

Posted: Thu Mar 01, 2007 12:13 am
by Robert
Do you have A/C also or just Heat ?

If you have A/C also, switch t-stat to Cool and see if blower remains on through the cycle.

If so, you most likely just need a Sequencer.

Take care and best wishes,
Robert

RE: nordyne elec furnace part

Posted: Thu Mar 01, 2007 2:06 am
by rogerman123
NO I DON'T HAVE AC......I DID FORGET TO MENTION THAT THE REPAIR TEC THAT LOOKED AT MY UNIT SAID THE T-STAT WAS WIRED INCORECTLY. HE SWITCHED SOME OF THE CONNECTIONS AND THE UNIT RAN FOR A LITTLE LONGER BUT SOON STARTED TO CYCLE ON AND OFF AGAIN LIKE BEFORE.

RE: nordyne elec furnace part

Posted: Thu Mar 01, 2007 11:28 am
by Robert
Hi,

If this is the same person who quoted you $1,100 to repair it, can you tell me what color wire is connected to what letter terminal on t-stat?

Thanks,
Robert

RE: nordyne elec furnace part

Posted: Thu Mar 01, 2007 2:48 pm
by rogerman123
IT WAS THE SAME PESON WHO GAVE ME THE ESTIMATE.....I WILL GET YOU THE INFO LATER TODAY WHEN I GET HOME FROM WORK.....THANKS FOR YOUR HELP

RE: nordyne elec furnace part

Posted: Thu Mar 01, 2007 4:53 pm
by Robert
Hi,

You're very welcome. With that absurd estimate, I tend to not trust this guy and want to be sure he has not done something dishonest.

Although, that estimate itself was dishonest .

Thanks,
Robert

RE: nordyne elec furnace part

Posted: Thu Mar 01, 2007 10:09 pm
by rogerman123
The make of the t-stat is a White Rogers, I had the white wire connected to the WH terminal, and the red wire connected to the 4M terminal. He removed the red wire and put it to the RV terminal.
He left the white wire to the WH terminal. I hope that is what you need to know.......let me know, thanks......Roger

RE: nordyne elec furnace part

Posted: Fri Mar 02, 2007 2:45 am
by Robert
What is the model number of the t-stat ?

Had the furnace been working fine with the t-stat connected as you had it, then suddenly stopped ?

Thanks,
Robert

RE: nordyne elec furnace part

Posted: Fri Mar 02, 2007 11:12 am
by rogerman123
No it was malfunctioning when I got the house about eight months ago. I just now have had the time and money to fix things. At first when it was not working right I tried replacing the t-stat and filter, then is when I called the company to check it out. So its been doing the same thing the whole time.

RE: nordyne elec furnace part

Posted: Fri Mar 02, 2007 11:19 am
by rogerman123
Sorry I forgot the model #1F56-306 White Rogers

RE: nordyne elec furnace part

Posted: Sat Mar 03, 2007 1:46 am
by Robert
Hi,

That White-Rodgers T-Stat # 1F56-306 should have the following terminals:

4, W, R, Y, G

IF you only have two wires, the White goes to W and the Red to R.

I believe that is how it is wired now.

Do you have or have access to a Multi-Meter to test voltages and do you feel comfortable doing so ?

If so, you can test the sequencer and blower relay to see if they're faulty.

I believe that the sequencer is the problem, but w/o testing can't say for sure.

Without testing, I would suggest buying both the sequencer and blower relay and replacing them yourself for best chance of solving this problem.

The only absolute way is to test or call a reputable Tech, but based on what info you have given and my 27+ years in this business, I believe that the sequencer and blower relay both being replaced will resolve this issue.

I'm not there though, so can only give my advice based on the limited info I have.

If you have or can get a meter and want to test them, let me know.

Thanks,
Robert

RE: nordyne elec furnace part

Posted: Sat Mar 03, 2007 12:46 pm
by rogerman123
I do have a meter, but from what you have told me and the tec that was here I would like to just go ahead and replace the sequencers and relay. If you could give me the part #s I will order them from You?......are there two sequencers or just one?
Thanks so much for your help, after i get the parts installed I will let you know how it went..........Roger