Red led flashes three times, but pressure switch checks out, hoses clean, 27v. Yellow wire to gas valve body reads 14.6v clicks, reads 27v for split second and the system shuts down. Reading without yellow wire connected. When wire is connected I don't get a reading through eather yellow or brown wire.
Got any idea's or would this point to the gas valve? or control board? I would guess control board OK with the readings I got with the wire disconected.
Thanks
Tad
Nordyne M2RL080A-16B
Hi Tad,
Go to pressure switch and determine the input low voltage side wire (24-28vac).
You should have that voltage to ground.
Then, on a call for heat from t-stat, you should still have that, BUT should also have same reading from other side to ground.
IF you have those, then follow output wire to next connection and test from there to ground.
When you have voltage at one point, but not at next, it is either the wire between them or the component.
Thanks,
Robert
Go to pressure switch and determine the input low voltage side wire (24-28vac).
You should have that voltage to ground.
Then, on a call for heat from t-stat, you should still have that, BUT should also have same reading from other side to ground.
IF you have those, then follow output wire to next connection and test from there to ground.
When you have voltage at one point, but not at next, it is either the wire between them or the component.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
only 2 wires to gas valve. Should I have 24v reading at brown wire and same on yellow wire?
If those are the 2 wires at gas valve, you place one meter lead on one and other meter lead on the other.
You should read 24-28VAC with a call for heat after about 1-2 minutes.
Thanks,
Robert
You should read 24-28VAC with a call for heat after about 1-2 minutes.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 45263 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 31036 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-
-
- 2 Replies
- 23823 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 160641 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 37352 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-