E1EH-015HA fan does not run on during heating.
The heating elements turn on, but the fan does not. I have to turn the switch on the unit to ON from AUTO. The AC works fine the fan comes on in auto mode. I thought the heat relay might be bad on the circuit board so I unsoldered both relays and swapped them. Nothing changed the AC fan still works and the fan does not turn on during heating. It seems from reading the posts that the sequencer is bad. I am sure it was replaced earlier in the year when we moved into the home. Do sequencers go bad that quickly? If not what could cause the sequencers to go bad? The mobile home is about 12 years old. What would be the replacement sequencer for the above model? It has 308840 marked on the body and H1-110 and C1-110 on the mounting bracket. Thanks for your help.
Hi,
The sequencer controls both the elements and the blower for heating mode.
Sequencer # 621383
Sequencer # 621696
Both can be seen and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
621696 controls blower if they are wired correctly.
Thanks,
Robert
The sequencer controls both the elements and the blower for heating mode.
Sequencer # 621383
Sequencer # 621696
Both can be seen and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
621696 controls blower if they are wired correctly.
Thanks,
Robert
Last edited by Robert on Fri Dec 26, 2008 8:52 pm, edited 1 time in total.
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
We try to keep one question only per thread, so please start a new thread with your questions.
Once done, you can come back here and delete your post here.
Thanks,
Robert
We try to keep one question only per thread, so please start a new thread with your questions.
Once done, you can come back here and delete your post here.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 38219 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 162934 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Can't read MFD size on rusted dual run cap.
by justplumducky » Sat Jul 01, 2017 6:31 pm » in Nordyne Service & Repair - 0 Replies
- 45344 Views
-
Last post by justplumducky
Sat Jul 01, 2017 6:31 pm
-
-
- 2 Replies
- 25991 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
- 0 Replies
- 31467 Views
-
Last post by clsmatHH
Wed Oct 16, 2019 12:43 pm