Thank you for this site!
I just spend some time reading past posts and I think I have it but want to double check with the expert's before laying down cash for parts.
I have the above model Furnace and it has worked for years just fine heating my detached garage until this fall. Normally I have the thermostat set at 48 and it comes on after sitting idle waiting all summer. This year no go. I cycled it a few times and still no go, I hear it do the cycle, but no heat.
Popping the cover I noticed that the Hot Surface Igniter 1018 flashes 3 times at me after a failed cycle. I looked through the peep-hole and didn't see anything glowing during a cycle. I opened up the furnace and pulled the burner out and everything looked OK. I check the electrical connections and everything looks tight and clean. When the furnace is running a start cycle I can smell gas if I hold the peep hole open.
3 flashes you have indicated in other posts is typically a bad ignitor or flame sensor which the no glow on a start signal would also indicate. It shouldn't be the gas valve if I can smell gas on the attempt to start. Am I thinking about this right?
Is there a way to test the ignitor or is it a just replace and see if it fires item?
Thanks for the help!
Chewman
MMHB-090ABHR-06 Will not fire up
Hi,
Follow wires from ignitor to plug connector, disconnect, place meter leads in furnace plug, set t-stat to call for heat, wait about a minute or so and see if you get a reading of 120vac.
IF you do and ignitor was not energizing, it is bad.
Let me know what it reads and I'll give ordering info if needed.
Thanks,
Robert
Follow wires from ignitor to plug connector, disconnect, place meter leads in furnace plug, set t-stat to call for heat, wait about a minute or so and see if you get a reading of 120vac.
IF you do and ignitor was not energizing, it is bad.
Let me know what it reads and I'll give ordering info if needed.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Ignitor # 902661A can be seen and ordered through Paypal
from right side of page here :
http://www.mobilehomerepair.com/NordyneGas.html
Thanks,
Robert
Ignitor # 902661A can be seen and ordered through Paypal
from right side of page here :
http://www.mobilehomerepair.com/NordyneGas.html
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Thanks Robert!
Just ordered the igniter. I will let ya know how it works out!
Thanks again for all the help!
Chewman
Just ordered the igniter. I will let ya know how it works out!
Thanks again for all the help!
Chewman
Got the ingnitor yesterday, had it installed in about 15 minutes and had heat!
Thanks for the great help!
Chewman
Thanks for the great help!
Chewman
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 70300 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 110944 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Heat strips are on, but not the fan.
by Forestbrook » Sat Dec 08, 2018 6:09 pm » in Coleman Service & Repair - 0 Replies
- 39712 Views
-
Last post by Forestbrook
Sat Dec 08, 2018 6:09 pm
-
-
- 2 Replies
- 24599 Views
-
Last post by plumducky
Tue Dec 10, 2019 3:59 pm
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 159482 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-