pilot lights up and stays on. when thermostat turns furnace on, blower runs fine, furnace fires up, runs for about 30-40 seconds, then just as it seems like it is about to turn the fan on everything shuts off (burner and pilot) except for blower keeps running, and would keep running forever unless I turn down the thermostat. any ideas would be appreciated. Ricky
Hi,
Check burner and burner orifice for blockages. Check gas valve and see if it receives 24vac at all times during heat cycle once it gets original signal.
Thanks,
Robert
Check burner and burner orifice for blockages. Check gas valve and see if it receives 24vac at all times during heat cycle once it gets original signal.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 45631 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 31384 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-
-
- 2 Replies
- 24146 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 161507 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 37705 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-