E-2EB-015HB Fan and heat problems
a couple of days ago, my electric turn off ,do to some outage, when the electric was turn back on,i had problems with an and heat, my a/c works fine on auto and fan on, but when i put the heat on auto,nothing happens. when i put the heat on (fan on) the fan comes on but i get no hot air, can u please help. i really need a step by step troubleshooting, pics if you have them of parts and where i should be checking for voltage,or what you think i should check.thanks
Hi,
Possibly a bad contactor which controls the heating elements and the blower motor.
You can see and order Contactor # 621958 from top right here :
http://www.mobilehomerepair.com/Order4b.html
If you look at the ends, you see a set of two brass colored terminal spades on each side.
With a meter lead on one of the spades on each side, one end should read 240VAC and other end should read 0VAC.
Then, set t-stat to call for heat, test the side silver terminals and should read 24VAC.
IF so, you should now read 240VAC at the end that previously read 0VAC.
IF not, contactor is bad.
Thanks,
Robert
Possibly a bad contactor which controls the heating elements and the blower motor.
You can see and order Contactor # 621958 from top right here :
http://www.mobilehomerepair.com/Order4b.html
If you look at the ends, you see a set of two brass colored terminal spades on each side.
With a meter lead on one of the spades on each side, one end should read 240VAC and other end should read 0VAC.
Then, set t-stat to call for heat, test the side silver terminals and should read 24VAC.
IF so, you should now read 240VAC at the end that previously read 0VAC.
IF not, contactor is bad.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi,
Go to the link given to see it, click on pic for enlarged view.
It is the relay switch which energizes the elements and blower motor.
It is on back wall of controls compartment just above the heating element front plates.
Thanks,
Robert
Go to the link given to see it, click on pic for enlarged view.
It is the relay switch which energizes the elements and blower motor.
It is on back wall of controls compartment just above the heating element front plates.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Heat strips are on, but not the fan.
by Forestbrook » Sat Dec 08, 2018 6:09 pm » in Coleman Service & Repair - 0 Replies
- 40222 Views
-
Last post by Forestbrook
Sat Dec 08, 2018 6:09 pm
-
-
-
A/C and heat comes from the ceiling vents. Are the existing floor vents necessary?
by NanaMary » Tue Nov 21, 2017 12:35 pm » in All Other HVAC Questions - 2 Replies
- 52718 Views
-
Last post by NanaMary
Fri Nov 24, 2017 11:14 am
-
-
-
Heat exchanger walls and floor all sooted up.
by plumducky » Sat Jan 25, 2020 5:05 pm » in Coleman Service & Repair - 1 Replies
- 26953 Views
-
Last post by Filkinson
Tue Feb 18, 2020 9:01 am
-
-
- 0 Replies
- 43929 Views
-
Last post by chrismc_us
Mon Dec 23, 2019 9:00 am
-
-
2-combo single pole lightswitch problems
by hstassen » Mon Jan 06, 2020 9:41 pm » in Mobile Home Repair - 2 Replies
- 12803 Views
-
Last post by Greg
Tue Jan 07, 2020 6:12 pm
-