FEH-015HA Heater coil problem

Posted: Wed Apr 04, 2007 12:33 pm
by tiso_us
This is my first time posting. I have a Nordyne FEH-015H that I'm upgrading from a 012H Model, I'm also using a Honeywell T-Stat and a vary old one at that. Here's my problem, When I first hooked the FEH-015H up, the fan ran constant, elements and T-Stat worked fine, the blower however, would not shut down.

Day Two, decided to replace the Sequencer with another one. This time the blower shuts off with a sudden stop and the elements comes on ?????!. The Sequencer was from the old furnace (012H) which I know was working fine when i removed it. When I hooked the sequencer up, I noticed one of the hot black wires was wrong, instead of it being on the M4, it was on the bottom copper color lead, I then took it off and put it on M4.

A few little notes though, when i got the 015H unit, I would put the T-Stat on 60 degrees and put it on "Auto", the blower works but no heat. put it on 80 degrees and on "auto", I got heat but blower continues even after coils shuts down.

Also, on the sequencer, my wire diagram does not call for a wire lead across the bottom on one side, should i cut this wire, its been soldered in place?.

Thank you in advance.[/b]

RE: FEH-015HA Heater coil problem

Posted: Thu Apr 05, 2007 12:06 am
by Robert
Hi,

Do you have a/c or just heat ?

Bottom brass terminals are coil terminals. You'll either need the jumper or have low voltage wires from transformer connect to both sets on one side.

This could be a faulty sequencer, t-stat, blower relay if you have a/c or faulty Limits.

Did you upgrade the Limits also ?


Thanks,
Robert

RE: FEH-015HA Heater coil problem

Posted: Thu Apr 05, 2007 1:16 am
by tiso_us
Thanks Robert for the reply. Actually its a 'H' only according to the wiring diagram. the blower has 'HA' on it, of course i don't have AC with this unit.

the unit already had Limit switches in it so i just left it alone. I will attempt to test these tomorrow using a multimeter.

and thanks again for the reply.

RE: FEH-015HA Heater coil problem

Posted: Thu Apr 05, 2007 11:12 pm
by tiso_us
OK, OHMS testing the Limits resulted in 000 with beeping.

The T-Stat was replaced with new one.

Tested the OHMS on Sequencers from M1-M2 = nothing.

Tested the OHMS on Sequencers from M3-M4 = nothing.

Tested the OHMS on Sequencers from M5-M6 = nothing.

Tested the OHMS on 24V one was 074 resistance and the other was 086.

Voltage testing will be later tonight due to grandkids.

I suspect the Sequencer being faulty, at one time today, the furnace kicked on by itself but did not kick off, nonetheless it did kick on and with a little heat.

RE: FEH-015HA Heater coil problem

Posted: Sat Apr 07, 2007 3:05 am
by Robert
Are the Limits from the 012 or did they come with the 015 ?

The Limits for the two furnaces are different.

Thanks,
Robert

RE: FEH-015HA Heater coil problem

Posted: Mon Apr 09, 2007 3:57 am
by tiso_us
Robert, I found the problem and fixed it.......when you said limits on your last post, I began to trace the orange wire from the motor and there it was......the wire diagram said to run the orange wire to the fuse box, I took this orange wire and put it on the no.1 limit switch, now I have heat and blower working fine with t-Stat.

That just goes to show you can not always go by the wire diagram.

Thank you for the help, God bless. :D

RE: FEH-015HA Heater coil problem

Posted: Wed Apr 11, 2007 1:10 am
by Robert
You're very welcome. The wiring diagrams are almost always right, it's the colors that change and modifications and/or non OEM components that can throw it off.

Take care and best wishes,
robert