Page 1 of 1
INTERTHERM MODEL#P3RA-060K
Posted: Sun Feb 01, 2009 1:18 pm
by barker01
BLOWER MOTOR ONLY COMES ON WHEN SWITCHED TO THE ON POSITION WHEN IT IS THE HEAT SETTING. WORKS IN THE AUTO SETTING WHEN TURNED TO A/C
RE: INTERTHERM MODEL#P3RA-060K
Posted: Mon Feb 02, 2009 7:23 pm
by Robert
Hi,
Most likely a bad sequencer or contactor which controls the blower motor and heating elements in heat-auto mode.
Do you know what kw your heater kit is ? Or what the model number is of the heater kit ?
Thanks,
Robert
RE: INTERTHERM MODEL#P3RA-060K
Posted: Mon Feb 02, 2009 7:39 pm
by barker01
WHERE WOULD I FIND THE KW OR MODEL # INFORMATION LOCATION AT.
RE: INTERTHERM MODEL#P3RA-060K
Posted: Mon Feb 02, 2009 8:50 pm
by Robert
At the unit where the heater kit is at. May be on front plate or a model number/part number of heater kit.
May have to remove heater assembly to see how many element coils there are.
Thanks,
Robert
RE: INTERTHERM MODEL#P3RA-060K
Posted: Wed Feb 04, 2009 5:45 pm
by barker01
HEAR IS THE INFO I FOUND ON THE HEATER KIT KW 15 MODEL#H3HK015H VOLTS 208/240 AMPS 52/60 KW 10.8/14.4 HOPE THIS IS THE RIGHT THING YOU WERE LOOKING FOR.
RE: INTERTHERM MODEL#P3RA-060K
Posted: Thu Feb 05, 2009 12:13 am
by Robert
Hi,
Yes, that is it and I'll get that info as soon as possible from distributor.
Thanks,
Robert
RE: INTERTHERM MODEL#P3RA-060K
Posted: Thu Feb 05, 2009 6:10 pm
by barker01
THANKS FOR LOOKING INTO THIS FOR ME
RE: INTERTHERM MODEL#P3RA-060K
Posted: Mon Feb 09, 2009 1:00 am
by Robert
Still waiting on reply from distributor, hopefully will hear something tomorrow.
Thanks,
Robert
RE: INTERTHERM MODEL#P3RA-060K
Posted: Tue Feb 17, 2009 1:59 pm
by Robert
Hi,
Sorry for delay, received reply while down sick and just now
recovered enough to get back on.
Heater Kit # 917172B @ $236.00 + $8.00 shipping can be ordered
with Visa or MasterCard by calling toll free to 1-877-263-7860 .
It can be shipped immediately from distributor.
Thanks,
Robert