Nordyne Modle # E2EB-015HA will not come on

Posted: Mon Feb 16, 2009 1:45 pm
by Mike Lumry
My furnace quit two weeks ago so Ii replaced the thermostat. Has worked great for two weeks. Came home from Tulsa last night and it quit again. I think it may be the low voltage trans but not sure. It has 120v going in each side on the bottom and 25.6v on the top left and 3.5v on the top right. Should the top right be 24v also?

RE: Nordyne Modle # E2EB-015HA will not come on

Posted: Tue Feb 17, 2009 6:27 pm
by Robert
What do they read across them ?


Primary-Line side = 240vac across them.

Secondary-Load side = 24vac across them.


This is most likely a faulty sequencer problem.


Sequencer # 01-0843 can be seen and ordered through PayPal

from right side of page here :

http://www.mobilehomerepair.com/NordyneElec.html



Thanks,
Robert