I need to replace the sequencer in my unit but after reading several posts I'm confused as to which one to order. I've seen both 01-0842 and 01-0843 suggested for that model. The numbers on my sequencer are;
T-O-D
H24V
12S22 308850
L9802
H24V
12S20 308495
L9802
Any help would be greatly appreciated. Thanks for a great site, it has helped volumes, except for this
Nordyne E2EB-15
Hi,
01-0842 was the original used, but 01-0843 is now the p/n recommended by Nordyne.
I used to always go with what was listed by Nordyne, but then had a few people go to order and seen their furnace listed with the 01-0842.
So, to stop confusion went to telling them 01-0842.
EITHER will work fine. 01-0842 is a 3 contact set sequencer which is needed.
01-0843 is a four set, so one is left unused.
These are new p/n's and part designs. The old ones, the 3 set type was being phased out when they stated suggesting the 4 set type.
Now, if this has not confused you, order either and enjoy the heat.
Thanks,
Robert
01-0842 was the original used, but 01-0843 is now the p/n recommended by Nordyne.
I used to always go with what was listed by Nordyne, but then had a few people go to order and seen their furnace listed with the 01-0842.
So, to stop confusion went to telling them 01-0842.
EITHER will work fine. 01-0842 is a 3 contact set sequencer which is needed.
01-0843 is a four set, so one is left unused.
These are new p/n's and part designs. The old ones, the 3 set type was being phased out when they stated suggesting the 4 set type.
Now, if this has not confused you, order either and enjoy the heat.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Didn't know if I needed to start a new topic or not. Yesterday the main 200 amp breaker for the house popped and a burnt smell came from the AC/Heater area. Upon inspection the new sequencer I replaced early in the month has basically exploded and burned several wires completely through. It's been working without issue until this. I'm not sure where to start finding the trouble, was it the sequencer or something else causing it to go out? Where do I start?
Thanks,
Thanks,
Hi,
I would call a reputable licensed electrician out to ensure the correct fault and diagnosis is found.
With the main breaker kicking, would need to inspect wire cable from service panel to furnace IF main breaker is in the home service panel.
IF it is in outside panel at service pole, need to also inspect wire cable from there to inside home service panel.
IF not found there, then call an hvac tech to inspect furnace.
This "sounds" like an overheated wire cable possibly kicking the breaker and the condition overheated and melted the sequencer.
Will take thorough voltage and amperage tests to find the cause.
Due to high possibility of fire if not diagnosed correctly, I would place this in the hands of above mentioned pros.
Thanks,
Robert
I would call a reputable licensed electrician out to ensure the correct fault and diagnosis is found.
With the main breaker kicking, would need to inspect wire cable from service panel to furnace IF main breaker is in the home service panel.
IF it is in outside panel at service pole, need to also inspect wire cable from there to inside home service panel.
IF not found there, then call an hvac tech to inspect furnace.
This "sounds" like an overheated wire cable possibly kicking the breaker and the condition overheated and melted the sequencer.
Will take thorough voltage and amperage tests to find the cause.
Due to high possibility of fire if not diagnosed correctly, I would place this in the hands of above mentioned pros.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 58773 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 38229 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
Nordyne M1MB clicks 4 times when starting
by olsonlaaa » Thu Aug 24, 2017 10:54 am » in Nordyne Service & Repair - 0 Replies
- 41715 Views
-
Last post by olsonlaaa
Thu Aug 24, 2017 10:54 am
-
-
-
Help with Nordyne electronic board
by swade1991 » Thu Aug 02, 2018 12:13 pm » in Nordyne Service & Repair - 0 Replies
- 27753 Views
-
Last post by swade1991
Thu Aug 02, 2018 12:13 pm
-
-
- 2 Replies
- 20605 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:35 am