furnace blowing cold
Posted: Wed Mar 04, 2009 7:35 pm
by expoman1997
I have a nordyne furnace #E2EB 010. Due to a recent short in the system. I have replaced the Blower motor, blower relay, and sequencer. Since then it will blow warm air sometimes. Usually it blows normal cool air. Should I have replaced the Limit switch too? Is that the problem? Thanks
RE: furnace blowing cold
Posted: Thu Mar 05, 2009 1:47 am
by Robert
Could be a bad/open limit, bad element, bad breaker or wiring (burnt) problem.
Thanks,
Robert
Posted: Thu Mar 05, 2009 2:54 am
by expoman1997
All of the wires are new also. Also the outside heat pump is not working. I opened the cover on my thermostat and notice a burn mark on the white wire at the soder point on the top mercury tube with the green tip. The only way i am getting heat is when the bottom mercury tube with orange tip activates im guessing that is the emergency heat. Thanks
RE: furnace blowing cold
Posted: Fri Mar 06, 2009 1:01 am
by Robert
Hi,
T-stat will need replacing, not sure if that is all though without being there.
Thanks,
Robert