Blower will not start

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
ESCHE
Posts: 4
Joined: Fri Oct 17, 2008 12:06 pm
Location: INDIANA

Hi,
I have a Coleman Presidential II modle#3118B750. My blower will not start unless I use the manual switch on the side of the blower. I replaced the blower switch 3115a330 with bolwer switch 3115a3301. The same result still. The new switch made a series of clicking noises that the old one did not. I made sure all wires from one switch connected the the same numbered terminals as the new switch. Any ideas would be great. Thanks.
ESCHE
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

IF you have 24vac low voltage supply, then most likely a bad sequencer.


Sequencer # 3115-3571 can be seen and ordered through PayPal

from right side of page here :

http://www.mobilehomerepair.com/ColemanElec.html


Do you have a wiring diagram ?

If you do and take a pic and send to my email, I'll see if anything else:

[email protected]


Thanks,
Robert