Hi,
I have a Coleman Presidential II modle#3118B750. My blower will not start unless I use the manual switch on the side of the blower. I replaced the blower switch 3115a330 with bolwer switch 3115a3301. The same result still. The new switch made a series of clicking noises that the old one did not. I made sure all wires from one switch connected the the same numbered terminals as the new switch. Any ideas would be great. Thanks.
Blower will not start
Hi,
IF you have 24vac low voltage supply, then most likely a bad sequencer.
Sequencer # 3115-3571 can be seen and ordered through PayPal
from right side of page here :
http://www.mobilehomerepair.com/ColemanElec.html
Do you have a wiring diagram ?
If you do and take a pic and send to my email, I'll see if anything else:
[email protected]
Thanks,
Robert
IF you have 24vac low voltage supply, then most likely a bad sequencer.
Sequencer # 3115-3571 can be seen and ordered through PayPal
from right side of page here :
http://www.mobilehomerepair.com/ColemanElec.html
Do you have a wiring diagram ?
If you do and take a pic and send to my email, I'll see if anything else:
[email protected]
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 14 Replies
- 160996 Views
-
Last post by Greg
Tue Sep 26, 2017 1:00 pm
-
-
3500A816 Randomly wont start or shut down
by Smithcraft » Fri Jan 13, 2023 4:04 pm » in Coleman Service & Repair - 0 Replies
- 91010 Views
-
Last post by Smithcraft
Fri Jan 13, 2023 4:04 pm
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 111378 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 160127 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 70688 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-