My father in law has an old Intertherm P3RA-030K cooling only unit that he got from a friend. He needs to know what amperage it is. The info tag on the unit is faded off so he can not see what it is. If you need any info let me know and I will relay the info back and forth and he is not too computer literate.

Thanks,
Allen

RE: Nordyne Intertherm Amp question??

Posted: Mon May 25, 2009 6:17 pm
by Robert
Hi Allen,

Minimum Circuit Ampacity = 20.4

Total Unit Amps = 17.0


Compressor RLA = 13.7

Compressor LRA = 75.0

Condenser Fan Motor Amps = 1.2

P- Single packaged a/c unit
3- design series
R- round duct
A- 10 seer
030 = 30,000 btu's = 2.5 tons
K- 208/230vac-60HZ-1 phase



Thanks,
Robert