Glad I found this forum. I have a 2 yr old Intertherm M3RL 060A furnace with NO A/C. Problem is the blower speed is really high! And very distracting in my small trailer, as you can imagine. Looking at the manual, Figure 27, shows the location of the speed taps on the circuit board on the lower right. I see an orange wire connected to tap M1, no wire to M2, a blue wire to M3, a red wire to HEAT, and a black wire to COOL. Thanks for any help here on which wire/s to pull or switch over.
Gary
Need to lower blower speed on M3RL
Hi Gary,
M1= Blue
M2= Orange
M3= Black now on COOL
HEAT= Red
COOL= Nothing
EAC= Nothing
XFMR= Black from transformer
L1= Black from deck switch
Be sure that there is not a jumper across/between HEAT and COOL
Thanks,
Robert
www.mobilehomerepair.com
M1= Blue
M2= Orange
M3= Black now on COOL
HEAT= Red
COOL= Nothing
EAC= Nothing
XFMR= Black from transformer
L1= Black from deck switch
Be sure that there is not a jumper across/between HEAT and COOL
Thanks,
Robert
www.mobilehomerepair.com
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Gary,
You're very welcome, happy to help. That is correct wiring without a/c . IF there is a problem now, it will be elsewhere other than location of wiring.
Thanks,
Robert
You're very welcome, happy to help. That is correct wiring without a/c . IF there is a problem now, it will be elsewhere other than location of wiring.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm M3RL series 90+ Downflow
by CatherineGramze » Mon Nov 26, 2018 4:16 pm » in Nordyne Service & Repair - 1 Replies
- 21753 Views
-
Last post by Aiden4584
Thu Feb 21, 2019 2:48 am
-
-
-
Eb12eb Coleman furnace 4 speed help.
by Johnwayne892000 » Thu Aug 30, 2018 7:37 pm » in Coleman Service & Repair - 0 Replies
- 21825 Views
-
Last post by Johnwayne892000
Thu Aug 30, 2018 7:37 pm
-
-
-
Need advice on blower
by NorthTexasSafariGuy » Mon Jul 31, 2017 9:18 am » in Coleman Service & Repair - 0 Replies
- 65908 Views
-
Last post by NorthTexasSafariGuy
Mon Jul 31, 2017 9:18 am
-
-
-
Need to remove a stripped Allen wrench-type plug from the OUT PRESS port on top of gas valve
by justplumducky » Fri Aug 25, 2017 8:21 am » in Nordyne Service & Repair - 1 Replies
- 44631 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:29 am
-
-
-
Need help identifying manufacturer of back door
by nestsman » Mon Oct 09, 2017 11:25 am » in Mobile Home Repair - 2 Replies
- 21518 Views
-
Last post by UmpJJ
Wed Oct 18, 2017 8:48 am
-