Our heating element is staying on at all times, even when the A/C is running. What could be causing this problem? An electrician at work mentioned it could be a relay? We have temporarily disconnected the heat so the house doesn't burn down, but it's starting to get chilly at night...
Thanks!!!
Sarah
Nordyne model E2EB-015HA - relay problem?
Hi Sarah,
That is usually one of two things, either an element coil has fallen down touching other elements or the sides of frame.
Or, the sequencer is bad.
You can remove the screws along bottom side flanges at blower housing, disconnect the wiring harness/connections, then carefully slide it out.
Look down inside to see elements and if they have fallen or are ok.
Sequencer # 01-0842 can be seen and ordered through PayPal from left side of this page :
Thanks,
Robert
www.mobilehomerepair.com
That is usually one of two things, either an element coil has fallen down touching other elements or the sides of frame.
Or, the sequencer is bad.
You can remove the screws along bottom side flanges at blower housing, disconnect the wiring harness/connections, then carefully slide it out.
Look down inside to see elements and if they have fallen or are ok.
Sequencer # 01-0842 can be seen and ordered through PayPal from left side of this page :
Thanks,
Robert
www.mobilehomerepair.com
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Replace relay for Emergency. Heat in E2EB-15HB
by istvv4848 » Tue Oct 23, 2018 10:49 am » in Nordyne Service & Repair - 0 Replies
- 38690 Views
-
Last post by istvv4848
Tue Oct 23, 2018 10:49 am
-
-
-
Question about burned wiring on e2eb-015ha
by thomasclay » Thu Sep 14, 2017 5:37 pm » in Nordyne Service & Repair - 0 Replies
- 59242 Views
-
Last post by thomasclay
Thu Sep 14, 2017 5:37 pm
-
-
- 0 Replies
- 103880 Views
-
Last post by tph31850
Sun May 03, 2020 7:35 pm
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 151798 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 34132 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-