new contactor
we recieved the contactor still isnt working properly also when T stat is on auto it kicks on and off every few seconds but when we turn T stat to on it stays on is the T stat the problem or is it something else the.(furnace is a Nordyne E2EB-012HB) Thanks Shelly
Hi Shelly,
With a new contactor not resolving it, will most likely be one of the two relays. The two relays and the contactor are the components in the circuit along with the t-stat.
The contactor and the two relays are the usual culprits, sometimes one only and sometimes more than one.
Relay # 621898 and 621899 can both be seen and ordered through Paypal from this page:
http://www.mobilehomerepair.com/NordyneElec.html
The only way to know for certain though is to test the complete circuit with a meter until fault is found.
Thanks,
Robert
With a new contactor not resolving it, will most likely be one of the two relays. The two relays and the contactor are the components in the circuit along with the t-stat.
The contactor and the two relays are the usual culprits, sometimes one only and sometimes more than one.
Relay # 621898 and 621899 can both be seen and ordered through Paypal from this page:
http://www.mobilehomerepair.com/NordyneElec.html
The only way to know for certain though is to test the complete circuit with a meter until fault is found.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Shelly,
You're very welcome, happy to help. Here in the forums and in private emails, what is free or not depends on what is needed or how in depth the questions are.
When I do charge a fee, it is $20.00 for a 1 hour email session.
Unlike the other forums here, the four hvac forums are actually part of my employment income.
So I have to base my time accordingly.
If you click on hvac in the blue toolbar above, then click on articles when it changes to green, you'll find several free and helpful articles on hvac info.
Hopefully this takes care of it.
Thanks,
Robert
You're very welcome, happy to help. Here in the forums and in private emails, what is free or not depends on what is needed or how in depth the questions are.
When I do charge a fee, it is $20.00 for a 1 hour email session.
Unlike the other forums here, the four hvac forums are actually part of my employment income.
So I have to base my time accordingly.
If you click on hvac in the blue toolbar above, then click on articles when it changes to green, you'll find several free and helpful articles on hvac info.
Hopefully this takes care of it.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 2 Replies
- 46750 Views
-
Last post by Mark440
Thu Apr 11, 2019 11:15 am
-
-
New Deck and Porch coming (photos included)
by vilmel2vilmel2 » Mon Jul 17, 2017 5:58 pm » in Mobile Home Repair - 4 Replies
- 39687 Views
-
Last post by vilmel2vilmel2
Wed Aug 02, 2017 10:29 am
-
-
- 4 Replies
- 7328 Views
-
Last post by Norm Frechette
Thu Sep 07, 2017 5:27 am
-
- 2 Replies
- 3609 Views
-
Last post by Greg
Mon Sep 11, 2017 6:27 pm
-
- 10 Replies
- 83126 Views
-
Last post by Heathicus
Wed Oct 04, 2017 4:44 pm