Hi,
Hope you can help me. Heater is a around a 1991 Intertherm electric model #FEH-020HA-04.
Problem: Low heat temp. Heater Goes through all cycles fine.
Did some tests with meter.
transformer-240v on line side. around 26v on load side
sequencer no call for heat...
h1/h2=0vac
h3/h4=0vac
all m terminals to ground=120vac
m1/m2=240vac
m3/m4=240vac
m5/m6=240vac
m7/m8=240vac
sequencer with call for heat
h1/h2 and h3/h4= around 26vac
m1/m2,m3/m4=0vac
m5/m6 and m7/m8=240vac
this is where I think the problem is. This side of the sequencer is connected to the bottom 2 heat coils the are not coming on. the top 2 coils are on and are connected to the m1/m2 side on the sequencer.
With call for heat top 2 coils read 240vac across terminals
bottom 2 coils read 0 vac
I hope this info helps. So do I need a new sequencer? If so which one.
Also should I replace the 2 Limit Switches? Which part numbers would I need to order?
Thanks for the help
Bob
Intertherm Electric
Hi Bob,
Sequencer # 901076
(2) Limit Switches # 626409
The sequencer is bad and you have the above two limits. All can be seen
and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
Shipping is $8.00 .
Thanks,
Robert
Sequencer # 901076
(2) Limit Switches # 626409
The sequencer is bad and you have the above two limits. All can be seen
and ordered through PayPal from this page :
http://www.mobilehomerepair.com/NordyneElec.html
Shipping is $8.00 .
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
Hi Bob,
That's the price difference the manufacturer puts on them. Usually older means more $$$ due to shelf time.
Thanks,
Robert
That's the price difference the manufacturer puts on them. Usually older means more $$$ due to shelf time.
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
-
- Similar Topics
- Replies
- Views
- Last post
-
- 3 Replies
- 35220 Views
-
Last post by David DeBord
Sun Oct 22, 2017 8:16 am
-
-
Electric water heater, standard VS. MH specific
by ferret13sj » Thu Aug 26, 2021 3:41 am » in Mobile Home Repair - 4 Replies
- 40718 Views
-
Last post by Sulteric
Sun Sep 05, 2021 9:39 pm
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 46101 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 64923 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 104786 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-