Model # M1MB-070A-BW

Posted: Mon Nov 30, 2009 4:32 pm
by Mikew
This unit starts and runs just fine, But I do not think the flame is correct. There is blue right at the regulator outlet and lots of orange surrounding it. Seems to take a long time to heat the 1350 sq ft. home. Should there be any orange in the combustion area. There is no AC attached currently.

It is running on propane and propane configuration is in place

MIke :?:

Re: Model # M1MB-070A-BW

Posted: Wed Dec 02, 2009 3:45 pm
by Robert
Hi,


Check your main burner orifice for blockage from spider/web . Should be blue with slight orange tip at most.



Thanks,
Robert

Re: Model # M1MB-070A-BW

Posted: Fri Dec 04, 2009 12:51 am
by Mikew
Thanks, we will be going up in the next couple of weeks and pull it out and check / clean it

Re: Model # M1MB-070A-BW

Posted: Fri Dec 04, 2009 5:33 am
by Robert
Let me know what is found.


Thanks,
Robert

Re: Model # M1MB-070A-BW

Posted: Sat Dec 26, 2009 9:03 pm
by Mikew
Robert
we just got home, the burner was clean. I did spend more time looking at the flame. It is blue out of the burner, then when it strikes the plate it turns orange.

Also the temp coming out of the closest outlet was 101.

mike

Re: Model # M1MB-070A-BW

Posted: Sat Dec 26, 2009 10:07 pm
by Mikew
Also the burner is honey combed.

Re: Model # M1MB-070A-BW

Posted: Sat Dec 26, 2009 11:11 pm
by Robert
Hi Mike,

Did you check the roof-jack and flue by any chance ?


What was the return air temp at furnace ?



Thanks,
Robert

Re: Model # M1MB-070A-BW

Posted: Sun Dec 27, 2009 1:51 am
by Mikew
Did not check roof jack, This was installed by fuqua when they made the home.

the return air temp was probably about 70-73.

mike

Re: Model # M1MB-070A-BW

Posted: Sun Dec 27, 2009 1:58 am
by Mikew
I think I might be wanting more from this unit than it is capable of. When we go up in the winter it is 40 inside the home and the air coming out the registers is basically warm. We also light the wood stove fire and withing two hours with both units going the temp it up to 73-75 in the living area.

square feet in 1350 with normal peaked ceilings. so have a lot of space to get warm.

Re: Model # M1MB-070A-BW

Posted: Sun Dec 27, 2009 2:57 am
by Robert
Look on the data sticker or nameplate and see if it gives the designed temp. rise.


Usually, about 40* rise minimum, which would mean you should have another 10 to 12 degrees at least.


Thanks,
Robert

Re: Model # M1MB-070A-BW

Posted: Sun Dec 27, 2009 1:37 pm
by Mikew
From the service manual.

temp rise is 45-75 degrees.

Re: Model # M1MB-070A-BW

Posted: Sun Dec 27, 2009 7:52 pm
by Robert
Then it is 15 to 17 degrees below normal supply minimum temp.


I would get a hvac tech out to look at it.


Thanks,
Robert

Re: Model # M1MB-070A-BW

Posted: Mon Dec 28, 2009 12:20 am
by Mikew
Thanks for all your help, I will try and find one that can work on it.

mike

Re: Model # M1MB-070A-BW

Posted: Mon Dec 28, 2009 8:30 pm
by Mikew
Service on Thursday will let you know what is found,

mike

Re: Model # M1MB-070A-BW

Posted: Tue Dec 29, 2009 1:17 am
by Robert
Thanks Mike.


Take care and best wishes,