I have a Nordyne Furnace mgha-056abfc-01.
serial # MCH 9203-03841
Must be about 15 yrs old.
I put in a new thermostat and it checks out, but the burners don't ignite.
Pilot is lit and looks strong. AC works.
Help!

Re: burners won't ignite

Posted: Tue Dec 08, 2009 8:16 am
by Robert
Hi,

With a call for heat from t-stat, do you get 24VAC at the gas valve terminals ?


Thanks,
Robert

Re: burners won't ignite

Posted: Tue Dec 08, 2009 11:12 am
by DottieR
Are you replying to my question? I have no idea what you are talking about. You will have to talk in the most simple terms possible. When I try turn on the heat at the thermostat, there is a click at the furnace. that is all I can tell you.

Re: burners won't ignite

Posted: Tue Dec 08, 2009 10:34 pm
by Robert
Hi,

Yes and unfortunately, that is as simple of terms as it gets. If not understood, then trying to do DIY furnace repair is not a wise choice.


I would advise calling an hvac contractor out to diagnose and resolve the issue.