Nordyne heat constantly kicks off

Posted: Thu Dec 10, 2009 9:29 am
by brandonm_13
M1MC 090A BW

I have a Nordyne heater. Part of the time, the heater won't light apparently, because I notice it's not on and it has 4 blinnking red lights. Some of the time it lights and runs but the blower isn't working right. I"ve checked and the electronic ignition lights the pilot light. Then after a few seconds the fuel is pushed in and it lights. I will get a solid yellow light, and then after about 10 seconds the yellow light starts blinking. The flame keeps going until the blower starts. The instant the blower kicks on, the flame kicks off. After a few minutes it tries to kick on, but can't seem to stay on.

Re: Nordyne heat constantly kicks off

Posted: Thu Dec 10, 2009 10:43 pm
by Robert
Hi,

Check the main burner orifice to ensure there are no blockages such as a spider/web.

If ok and clear, then I would suspect the ignitor first and gas valve next.


The red blinking light is due to ignition failure and yellow blinking is due to weak flame.


You do not have a pilot light , the ignitor just ignites the gas as it comes through the burner.



Thanks,
Robert

Re: Nordyne heat constantly kicks off

Posted: Fri Dec 11, 2009 5:29 pm
by brandonm_13
I'll check that, but I've had nothing but problems with this unit since it was new 5 years ago.

One note about the pilot. I was watching this through the small flip cover at the front. I do have an electronic ignition that lights a pilot light. The pilot light stays lit for about 10 seconds before fuel is pushed through, which is then ingited by the flame. I don't know if it's not called a pilot light, but it's a small, eletconically lit flame that is about the same size as a cigarette lighter flame.

Anyway, I expect something els has gone bad. The first winter is the only winter I haven't had a problem with this unit.

Re: Nordyne heat constantly kicks off

Posted: Mon Dec 14, 2009 1:43 am
by Robert
Hi Brandon,

Haven't checked, but you probably have a two step gas valve which opens at a low fire stage and then opens fully to full fire stage.


That would explain what you are seeing because there is no pilot or anything else for ignitor to light except the burner.


Take care and best wishes,
Robert

Re: Nordyne heat constantly kicks off

Posted: Thu Dec 17, 2009 10:17 am
by brandonm_13
That sounds about right. Anyway, things have been hectic and I haven't had much chance to look at it, other than cleaning the filter. I'm suspecting the gas valve, since it burns until exactly when the blower kicks on. Of course there might be something wrong with the circuitry, but who knows. I'll be able to take a better look at it this weekend.

Re: Nordyne heat constantly kicks off

Posted: Thu Dec 17, 2009 6:36 pm
by Robert
Hi,

Sounds good, just let me know.



Thanks,
Robert