Nordyne Model MIMA056AWBlower Runs constantly

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
RulTer
Posts: 1
Joined: Tue Dec 29, 2009 2:59 pm

My blower will not shut off. The burner seems to cycle on when needed but the fan keeps running after the burner shuts off. What should I be checking . ( Nordyne model MIMA056AW )
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Hi,

With t-stat set to heat-auto and temp met and blower does not shut off, test across control board W and C for 24VAC .

Then test across the Heat terminal wire(orange) and the 2nd Neutral terminal from the left (4 neutrals-2nd from left) for 120VAC.


IF you do not have 24vac at W and C, BUT do have 120vac at Heat and Neutral, the board is bad.


Integrated Control Board # 903429 can be seen and ordered from this page:

http://www.mobilehomerepair.com/NordyneGas.html



Thanks,
Robert