Re: Intertherm FEH 015HA-03 Blower will not start

Posted: Mon Jan 18, 2010 5:41 pm
by Robert
Hi Ricky,

Let me get caught up on some of these forum questions and read over what you wrote in last reply and then I'll give you some tests to do to get to bottom of your problem.


Thanks,
Robert

Re: Intertherm FEH 015HA-03 Blower will not start

Posted: Tue Jan 19, 2010 7:51 pm
by Robert
Hi Ricky,

What happened when you changed setting to HG and t-stat set to heat-auto-85* ?

Try it with jumper removed .



Thanks,
Robert

Re: Intertherm FEH 015HA-03 Blower will not start

Posted: Sun Jan 24, 2010 4:28 pm
by Ricky.Glenn
Robert

As you suggested, I tried the t-stat in HG ans it did not correct the problem. With the jumper removed, the blower will come on when the t-stat is set to heat, and fan set to on.

Suggestions?

I received the relay and will install it.

Thanks

Ricky

Re: Intertherm FEH 015HA-03 Blower will not start

Posted: Mon Jan 25, 2010 4:51 pm
by Robert
Hi Ricky,

IF replacing the relay doesn't resolve it, then go to BOTH transformers and test each.

Primary-Line = 240vac

Secondary-Load = 24vac



Thanks,
Robert

Re: Intertherm FEH 015HA-03 Blower will not start

Posted: Mon Jan 25, 2010 10:13 pm
by Ricky.Glenn
Robert

The xfmr at the furnace has 24 vac when measured between the red wire going to the t-stat and the black wire going to the sequencer. There is 240 on the primary side.

I haven't checked the xfmr on the AC yet. But I will and will let you know.

With the t-stat set to HG, auto and set to demand heat with jumper removed the blower does not come on.

Regarding the relay, the one installed is an after market honeywell with 10 terminals. The one I ordered has only the six required terminals. The wiring schematic/diagram does not show the relay, but says install relay IAW diagram on relay. However, the OEM relay does not have a diagram. If possible, please identify where terminals 1 thru 6 on the relay should be connected.

Thanks

Ricky

Re: Intertherm FEH 015HA-03 Blower will not start

Posted: Tue Jan 26, 2010 2:05 am
by Robert
Hi Ricky,

1 = 24vac common side of transformer

3 = G on t-stat

5 = sequencer M 2

6 = Blower motor heat speed (low)

2 = furnace breaker

4 = Blower motor cool speed (high)


Thanks,
Robert