FEH-15/17A won't turn off

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
sc58
Posts: 2
Joined: Tue Jan 05, 2010 1:04 pm

I replaced the sequencer and thermostat. Unit will not shut off. i have turn it off at breaker. unit will wait a few minutes then come on. i also need a replacement disconnect assembly for it it melt part of it.
raydizzle34
Posts: 13
Joined: Wed Dec 17, 2008 12:12 pm
Location: Arizona

Does the blower stay on or is it the complete heating system?
sc58
Posts: 2
Joined: Tue Jan 05, 2010 1:04 pm

The whole unit stays on.
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

The elements and the blower remain on even after sequencer and t-stat was replaced ?


If so, recheck all the wiring to ensure wires to elements and blower are on the output side of sequencers.


Also look for shorted wires touching.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?