Nordyne model E1EH-015HA

Posted: Sun May 20, 2007 9:23 am
by hose6161
Hi Folks--- I have a Nordyne furnace that works ok (except for drawing lots of current) and a Evcon MBC48DQA Refrigeration Unit.
The outside A/C fan does not turn on at all. The A/C was unused for about 4 or 5 years until I moved it to my place and had the electricians hook it up. The fan turns freely when I spin it. The name and data plate are missing. Would any body have any ideas about Brand name or any good way to figger out repair or replacement. I have a 16X80 1997 Redman.
Thanks ,
Hose6161

RE: Nordyne model E1EH-015HA

Posted: Sun May 20, 2007 11:45 am
by hvac1000
Did you check the power supplied to the unit? Fuses and breaker ?

If it spins freely it is more than likely a power problem. Also make sure your thermostat is set for A/C use.

Next does the compressor kick in when the fan is not running?

Is the outdoor units contactor/starter pulling in?

Check for 24 volts to the outside unit on the control circuit line at the contactor/starter.

RE: Nordyne model E1EH-015HA

Posted: Mon May 21, 2007 3:16 am
by Robert
Hi,

Since it is a Coleman/Evcon A-Coil, outside Condenser is most likely Coleman/Evcon also.

That is a 4 ton a-coil which is most likely oversized for a 16X80 home.

I'm in a 16X80 and have a 3 ton.

Your blower motor in furnace may not support a 4 ton (1600 cfm).

Check all the things HVAC suggested and let us know.


Take care and best wishes,
Robert

RE: Nordyne model E1EH-015HA

Posted: Thu May 24, 2007 5:47 am
by hose6161
Thanks for the promp reply folks. I'll check those things when I go home in a coupla weeks( Right now i'm 440 miles from it)
Hose :wink:

RE: Nordyne model E1EH-015HA

Posted: Thu May 24, 2007 9:47 pm
by Robert
Hi Hose,

You're very welcome. Let us know when you can and we'll help all we can.

Take care and best wishes,
Robert