We have a 2 ton split system that we recently installed that runs fine for awhile then the high side begins to drop, run up, run up drop until finally the safety switch goes off on high pressure.

We replaced the filter/dryer thinking that there might have been a restriction or that the gentleman who brazed it applied to much heat since he has a bad habit of not using a wet rag during installation and has had filter/dryer problems in the past.

I am leaning towards a restriction in the high side, but am a bit thrown as sometimes the unit goes right into an extreme pressure on start up, sometimes it will run for 45 minutes before it does. It is providing normal cooling and we are not having anything freeze up on the lines or frost.

Right now we are considering replacing the 3/8 line, a-coil and filter dryer, but I hate being a parts changing monkey and would rather use this to learn and troubleshoot.