Intertherm E2EB transformers keep blowing

Questions about repairs and parts for Nordyne furnaces, air conditioners and heat pumps for manufactured homes including Intertherm, Mac and Miller brands. Click here for Nordyne parts.

Moderators: Greg, Mark

Locked
jcwing123
Posts: 1
Joined: Thu Sep 30, 2010 11:13 am

Hi, I have a Intertherm E2EB-023HA heater and I keep blowing 240/24 Volt transformers. I put a new one in (old one was blown, no 24V out), and in fan only mode the transformer held up, but when I switched to heat mode via the t-stat, the heater came on for about 3 seconds then blew the transformer. Funny thing is, the inline 3 amp fuse did not blow as you would expect from a high load on the 24V side.

Could this be from a possible shorted t-stat wire, a bad sequencer or relay pulling too much load? Or could i have gotten a bad transformer from the HVAC shop?
User avatar
Robert
Moderator
Posts: 6413
Joined: Wed Feb 28, 2007 12:07 am
Location: Tennessee

Most likely a short somewhere and with fuse not blowing, it needs to be checked by an hvac tech.


That is a type situation that can easily cause a fire.


Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?