E1EH-012 may need sequencer.

Posted: Fri Oct 29, 2010 5:23 pm
by Deathstryker
Recently, my Furnace has been blowing cold air with it set on heat setting. I've tested the 2 elements and I get resistance on both of them and they aren't grounded out. I've checked the wires and contacts and all seem good. Also, I've felt heat a couple of times from the elements during testing out of about 10 times I've turned it on. I'm starting to suspect that the sequencer is bad.

Trouble is, I can't find the exact part that goes in it. It's a 2-pole sequencer and the on/off times for it are 1-24 / 45-75 and these times seem to be hard to find in a sequencer. I read other posts on here and the "01-0840 Sequencer " on your guy's online store seems to be recommended but what are the on/off times for this sequencer?

Thanks,

Re: E1EH-012 may need sequencer.

Posted: Sun Oct 31, 2010 12:34 am
by Robert
Hi,

1 - 20 and 40 - 110 are the times. 01-0840 is the sequencer recommended by the furnace manufacturer.

Those times have a window and do change as new replacements are designed.


Sequencer # 01 - 0840 can be seen and ordered from here by paging down:

http://www.aberdeenhomerepair.com/store ... 8621696%29



Thanks,
Robert

Re: E1EH-012 may need sequencer.

Posted: Sun Oct 31, 2010 1:49 pm
by Deathstryker
Thanks for clearing that up, Robert.

Just now ordered one. Hope it's fixed after this.

Re: E1EH-012 may need sequencer.

Posted: Sun Oct 31, 2010 3:21 pm
by Robert
Hi,

You're very welcome, happy to help. Thanks for ordering.




Take care and best wishes,
Robert

Re: E1EH-012 may need sequencer.

Posted: Sun Nov 07, 2010 4:28 pm
by Deathstryker
I got the part in the other day and replaced it. My furnace is functioning again. Thanks again for your time, Robert.

Re: E1EH-012 may need sequencer.

Posted: Sun Nov 07, 2010 10:44 pm
by Robert
My pleasure, glad it's working again.



Thanks,
Robert