NORDYNE M1MB 070A BW

Posted: Tue Nov 02, 2010 12:36 am
by dwood165
FIRST AND FOREMOST THANK YOU IN ADVANCE FOR YOUR HELP. iI HAVE HAD A LOT OF PROBLEMS WITH THIS UNIT WHEN THE UNIT FIRES THE GAS VALVE CLICKS 4 OR FIVE TIME AS IT IS LIGHTING IS THIS WRIGHT I LIVE IN CASPER WY 5127 FEET ABOUT SEA LEVEL I PUT A #43 ORIFICE IN I LIVE IN A RULE AREA AND CAN'T GET LP DELIVERED SO I FILL 100LB TANKS WILL THEY BE ALL RIGHT TO RUN THIS UNIT THANK YOU DOUG

Re: NORDYNE M1MB 070A BW

Posted: Tue Nov 02, 2010 1:09 am
by Robert
Recheck your altitude and see if that is correct. It appears to be a mistype.


Thanks,
Robert

Re: NORDYNE M1MB 070A BW

Posted: Tue Nov 02, 2010 7:47 am
by dwood165
i checked casper wy Altitudes is 5123

Re: NORDYNE M1MB 070A BW

Posted: Tue Nov 02, 2010 7:49 am
by dwood165
dwood165 wrote:i checked casper wy Altitudes is 5123
Humbly Grateful

Re: NORDYNE M1MB 070A BW

Posted: Tue Nov 02, 2010 5:52 pm
by Robert
Hi,

The clicking is most likely the hot surface ignitor and it will often click a few times before lighting.

# 43 orifice is correct.

100 lb. tanks are ok so long as you have the LP regulated properly with correct gas pressure.



Thanks,
Robert