Page 1 of 1
Nordyne MMHA070ABHR05
Posted: Tue Nov 02, 2010 5:40 am
by abundas
Hi
Great site really appreciate the information here. When my furnace starts and the burner comes on it, the fan starts and stops anywhere from 2-4 time before it stays on. I recently found that when I remove the cover this goes away and once it starts it runs the full cycle normally. Any ideas greatly appreciated.
Thanks
Andy
Re: Nordyne MMHA070ABHR05
Posted: Tue Nov 02, 2010 6:47 pm
by Robert
Hi Andy,
Could be a bad fan switch, dirty burner tube, dirty/clogged burner orifice.
Thanks,
Robert
Re: Nordyne MMHA070ABHR05
Posted: Wed Nov 03, 2010 3:32 am
by abundas
Do you have any idea why it would work when the cover is off but the symtom comes back when I put the cover back on.
Thanks
Andy
Re: Nordyne MMHA070ABHR05
Posted: Wed Nov 03, 2010 4:31 pm
by Robert
Hi Andy,
Not without being there to see what is happening. Could be a combustion air problem.
How does the burner flame look when ignited ?
Thanks,
Robert
Re: Nordyne MMHA070ABHR05
Posted: Mon Nov 08, 2010 7:14 am
by abundas
At the end of the burner tube its blue and the flame in the chamber is a yellow/orange color.
Thanks
Andy
Re: Nordyne MMHA070ABHR05
Posted: Tue Nov 09, 2010 5:16 pm
by Robert
Thoroughly inspect the roof jack for blockages, separations or leaks.
Thanks,
Robert
Re: Nordyne MMHA070ABHR05
Posted: Wed Nov 10, 2010 6:50 pm
by abundas
Thanks again for your help I really appreaciate it, great site! I'll get up there and take a look.
Andy
Re: Nordyne MMHA070ABHR05
Posted: Thu Nov 11, 2010 3:35 am
by Robert
You're very welcome, happy to help.
Thanks,
Robert