Posted: Wed Dec 08, 2010 6:14 pm
by TONYd
I have an E2EB-017HA that will not turn on in auto. I have replaced the sequencer thinking that was the problem but its still not kicking on. The blower will work in the on position but not in auto and it will heat up. It has worked correctly a few cycles when i first replaced the sequencer but then it would not start back up. Is it posssibly a fan relay?

Re: Blower will not kick on in auto

Posted: Sun Dec 12, 2010 1:22 am
by Robert
Set t-stat to call for heat, wait 45 secs and then test and see if you have 240vac going to the heat speed wire and the common wire from breaker.


Usually red and orange or red and white from motor.

Is motor getting hot trying to start ?


Thanks,
Robert