Nordyne MMHA070ABHR-01 Gas Furnace
-
- Posts: 3
- Joined: Wed Nov 30, 2011 8:54 am
I searched the board but didn't find a post with a similar question. I tried to do the start up on my gas furnace in a mobile home today and the burner fan won't run. I have 120V to the furnace and the house blower fan runs fine on fan only mode. There is only 86 volts to the burner fan. Is this normal or does it indicate a control module problem? If normal, what do you suggest for my next trouble shooting step. Thanks.
-
- Posts: 3
- Joined: Wed Nov 30, 2011 8:54 am
Update: I did some more troubleshooting and was able to jumper the burner fan with 120V and it runs fine, so the burner fan itself is good. If its the control module, does anyone have a way to look up the replacement part number?
-
- Posts: 3
- Joined: Wed Nov 30, 2011 8:54 am
Update: The electronic control module was bad in my furnace. Just a note of caution to anyone who has the United Technologies 1018 Series Hot Surface Ignition modules, there are several versions of this module and they are not interchangeable. I was fortunate to ask a service tech a lot of questions and he pointed me to the correct one for my furnace. It works fine and I'm back in heat!
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Intertherm/Nordyne feh-015ha furnace issues blower not working, unit will only turn off at breaker box
by onmypath78 » Sat Mar 16, 2019 12:11 pm » in Nordyne Service & Repair - 0 Replies
- 158036 Views
-
Last post by onmypath78
Sat Mar 16, 2019 12:11 pm
-
-
-
Nordyne M1B1 furnace issue - thermostat c wire not hooked up correctly. It's running off atteries instead
by Tallestt » Mon Apr 20, 2020 6:27 am » in Nordyne Service & Repair - 1 Replies
- 39074 Views
-
Last post by taurolyon
Tue Jun 23, 2020 4:02 pm
-
-
-
I am thinking of switching to a gas water heater
by deryk the gypsy » Sat Jul 22, 2017 7:16 am » in Mobile Home Repair - 2 Replies
- 36079 Views
-
Last post by Greg
Sat Jul 22, 2017 12:26 pm
-
-
-
Need to remove a stripped Allen wrench-type plug from the OUT PRESS port on top of gas valve
by justplumducky » Fri Aug 25, 2017 8:21 am » in Nordyne Service & Repair - 1 Replies
- 45865 Views
-
Last post by Maxwell.lipphardt
Mon Feb 04, 2019 6:29 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 69468 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-