Intertherm mod feh015hr-03
electric furnace and air cond.Air has worked good all summer, turned on heat and it came on and worked ok for 1 day. Got up this am and turned thremo up for heat nothing happened at all ,tried air no go tried fan only no go will not do anything checked main breakers all are on.what do i check next??? thanks in advance for any answers.
Thanks for the reply,upon further inspection i found out that the fuse panel was the problem .One of the 60 amp fuses had blown due to the top of the fuse connector overheating and burning up the bakeolite panel where the connector was attached. I JB welded it back in place for the time being.I need a new panal. Mine has the 60 amp fuses on the inside and the 30 amp on the outside.Any ideas on a replacement??
-
- Similar Topics
- Replies
- Views
- Last post
-
-
Nordyne Mod. E1EH-015HA split unit/eliminate cooling?
by carolina jim » Thu Oct 24, 2019 8:33 am » in Nordyne Service & Repair - 0 Replies
- 36403 Views
-
Last post by carolina jim
Thu Oct 24, 2019 8:33 am
-
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 50219 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 69336 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 109847 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
- 0 Replies
- 74189 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm