the intertherm unit i am working on will just shut of and not come back on even when it drops below the temp setting on the termostat. they have to turn the breaker off then back on to get it to come back on. i have been told that it could be the sequencers just wanting a sec op on the matter
the model number is E2EH-012H
intertherm
Hi,
Make sure the sequencer bottom heater coils H1 and H2, H3 and H4 are getting the 24vac signal from t-stat.
If so, see if M1 and M2 contacts are closing to continue circuit for first element and blower motor.
Are the elements all getting 120vac at right side terminal from breaker through the limit ?
Thanks,
Robert
Make sure the sequencer bottom heater coils H1 and H2, H3 and H4 are getting the 24vac signal from t-stat.
If so, see if M1 and M2 contacts are closing to continue circuit for first element and blower motor.
Are the elements all getting 120vac at right side terminal from breaker through the limit ?
Thanks,
Robert
Some people are Humbly Grateful, while some are Grumbly Hateful.................... Which one are you ?
yes it is i have ordered the sequencers and yes it is getting 120 vac. im thinking that the contacts in side the sequencer are bad
-
- Similar Topics
- Replies
- Views
- Last post
-
-
intertherm standing pilot propane burner Heat Rise of 38°F spread.
by justplumducky » Fri Aug 25, 2017 10:06 am » in Nordyne Service & Repair - 0 Replies
- 55038 Views
-
Last post by justplumducky
Fri Aug 25, 2017 10:06 am
-
-
-
Intertherm standing pilot LPG burner 77 BTU IN gas valve mounting plate gets hot ( not warm).
by justplumducky » Sat Sep 09, 2017 3:34 am » in Nordyne Service & Repair - 1 Replies
- 74809 Views
-
Last post by Maxwell.lipphardt
Thu Nov 22, 2018 10:15 am
-
-
-
Intertherm outdoor a/c unit, blower not turning off. Model unknown rating plate is faded out.
by tkrueger » Sat May 05, 2018 8:57 pm » in Nordyne Service & Repair - 0 Replies
- 116353 Views
-
Last post by tkrueger
Sat May 05, 2018 8:57 pm
-
-
- 0 Replies
- 78330 Views
-
Last post by newguy47
Thu Aug 16, 2018 8:21 pm
-
-
heater blower intertherm feh-015ha-03
by newguy47 » Wed Oct 24, 2018 8:04 am » in Nordyne Service & Repair - 0 Replies
- 84659 Views
-
Last post by newguy47
Wed Oct 24, 2018 8:04 am
-