Nordyne AC Trouble

Posted: Tue Jun 16, 2009 2:26 pm
by packerbacker7964
Once unit reaches set point the condensor will shut off but the fan stays running and won't go off no matter where ever you move the thremostat. Jumpered out the limit switches to check for them being the problem and still no luck.

RE: Nordyne AC Trouble

Posted: Tue Jun 16, 2009 6:05 pm
by Robert
What is the furnace model number ? Most likely a bad fan relay.




Thanks,
Robert

RE: Nordyne AC Trouble

Posted: Tue Jun 16, 2009 9:38 pm
by packerbacker7964
m1mb070abw Model number
m1m981003448 Serial number

Funny thing is that if you keep the unit about 76 degrees it goes on/off on it's own. ANything close to 73 and it does the run after the compressor is off and just keeps running even if you move the stat above 80 degrees. Hell you can move it back and forth and it clicks but stays running. Thanks for your time and effort.

RE: Nordyne AC Trouble

Posted: Tue Jun 16, 2009 11:52 pm
by Robert
Hi,

Your unit has an integrated control board that controls the furnace blower motor during heat and cool modes.


When the home has reached set temp and the outside condensing unit shuts off, but indoor blower keeps running, do these tests :


Go to board terminals W, C, G, R and test across G and C for 24 to 28VAC .

Then go to terminals XFMR, L1, HEAT, COOL and test across COOL and one of the NEUTRAL terminals to the left for 120VAC .


Let me know what you get.



Thanks,
Robert

RE: Nordyne AC Trouble

Posted: Wed Jun 17, 2009 4:10 pm
by packerbacker7964
Don't have an amp meter at home right now. Now it clicks and when I beat the relay it starts to blink 1 time. Once I beat the living shit out of it again it glows a steady red but still runs the inside fan with the outside unit off.

RE: Nordyne AC Trouble

Posted: Wed Jun 17, 2009 5:31 pm
by Robert
Most likely a bad control board relay, which will require replacing the board.


You'll need a volt-ohm meter to do the tests.



Thanks,
Robert

RE: Nordyne AC Trouble

Posted: Thu Jun 18, 2009 2:43 pm
by packerbacker7964
When cooling with outside unit running I get these readings
Gray- 0V
Red-27V
Green-25V
White-4V

when the outside unit goes off and the fan motor stays running on the inside the fan changes to a lower speed (just a couple RPM's but slower I get Green at 0V.

RE: Nordyne AC Trouble

Posted: Thu Jun 18, 2009 11:44 pm
by Robert
At that same time with outside condenser off and indoor blower still running and Green reading 0VAC.


What do you read across COOL and one of the NEUTRALS ?


Thanks,
Robert